Salah Zantout
Mechanical
- Sep 7, 2022
- 4
Dear All,
This is my first post in this forum and after I have been following it for sometime now. I have really found it to be informative and helpful in so many ways so I genuinely thank each and everyone of you for your contribution.
I would kindly like to ask your help for the following:
I have a closed loop chilled water system. Machine Room including chiller package, circulating pumps and expansion tank will be all installed at the ground level. The highest level for the system is at 12meters height. Fluid here is PG 33% with supply/return temp -6degC/-2degC. Expansion tank with pressurization unit to be installed on pump suction line as close as possible to pump inlet to get all additive positive pressure from discharge to suction of pump. I have assumed 50kpa additive pressure over the highest point in the system for proper venting.
The lowest MAWP for the components at the floor level is the pump and PHE which are at 10bars (both are at floor level). Pump delivery is 41meters.
Now the thing is that I want to figure out:
1. What the Max System Working Pressure is to put it in expansion tank sizing formula. Cold fill pressure is static 12m + 0.5 bar for positive venting.
Acceptance factor= (max system working pressure absolute - cold fill pressure absolute)/ (max system work pressure absolute)
2. Safety relief valve setting for the system which I suppose needs to be at the tank location different
than the one installed for other for components.
3. How to choose the system working pressure.
Please let me know if the above is clear or requires further elaboration.
Thank you all in advance.
Ps. I have attached the engineering handbook extrol which I found really helpful.
This is my first post in this forum and after I have been following it for sometime now. I have really found it to be informative and helpful in so many ways so I genuinely thank each and everyone of you for your contribution.
I would kindly like to ask your help for the following:
I have a closed loop chilled water system. Machine Room including chiller package, circulating pumps and expansion tank will be all installed at the ground level. The highest level for the system is at 12meters height. Fluid here is PG 33% with supply/return temp -6degC/-2degC. Expansion tank with pressurization unit to be installed on pump suction line as close as possible to pump inlet to get all additive positive pressure from discharge to suction of pump. I have assumed 50kpa additive pressure over the highest point in the system for proper venting.
The lowest MAWP for the components at the floor level is the pump and PHE which are at 10bars (both are at floor level). Pump delivery is 41meters.
Now the thing is that I want to figure out:
1. What the Max System Working Pressure is to put it in expansion tank sizing formula. Cold fill pressure is static 12m + 0.5 bar for positive venting.
Acceptance factor= (max system working pressure absolute - cold fill pressure absolute)/ (max system work pressure absolute)
2. Safety relief valve setting for the system which I suppose needs to be at the tank location different
than the one installed for other for components.
3. How to choose the system working pressure.
Please let me know if the above is clear or requires further elaboration.
Thank you all in advance.
Ps. I have attached the engineering handbook extrol which I found really helpful.