I have some existing plans for a project built in 1957. The plans call for "SJ 146" steel joists to support the flat roof. I easily found the load tables associated with this steel joist designation in the 75-Year Steel Joist Manual, so I thought my job of analyzing the joists was going to be simple. Then I was given the attached picture of the joists and informed that the top and bottom chords are "T"-shaped not double angles. Could these steel joists actually be the "SJ 146" called for on the plans, or are these joists different? The depth of the joists are indeed 14 inches like the call out on the plans indicates. I have never seen joists with "T" chord members before. Are there any references that include this type of joist?
If they are the "SJ 146", I'm coming up with about a 67 psf capacity for the 26'-0" span. This capacity seems plausible. I was hoping for a design capacity of at least 45 psf.
Thanks for any input!
EIT
I have some existing plans for a project built in 1957. The plans call for "SJ 146" steel joists to support the flat roof. I easily found the load tables associated with this steel joist designation in the 75-Year Steel Joist Manual, so I thought my job of analyzing the joists was going to be simple. Then I was given the attached picture of the joists and informed that the top and bottom chords are "T"-shaped not double angles. Could these steel joists actually be the "SJ 146" called for on the plans, or are these joists different? The depth of the joists are indeed 14 inches like the call out on the plans indicates. I have never seen joists with "T" chord members before. Are there any references that include this type of joist?
If they are the "SJ 146", I'm coming up with about a 67 psf capacity for the 26'-0" span. This capacity seems plausible. I was hoping for a design capacity of at least 45 psf.
Thanks for any input!
EIT