T60 Overall(Block Diff) Protection Relay , Angle Winding Respect to ? 1

Status
Not open for further replies.

rayas91

Electrical
May 6, 2015
71
Replies continue below

Recommended for you

YnD11 means the secondary delta leads the primary wye by 30 degrees (11:00 on the clock face when the primary is at 12:00). Since you are using the delta winding as the reference, the wye winding lags by 30. Suggest using -30 for winding 2. This assumes your bushings are conventionally connected and the CTs are wye connected.
 
thanks stevenal, But I mean that I cant understand how ct polarity affects angles.

Can you give a clear example with CTs,like my drawing ?
 
ReallY Thank You , I understand now ..


Thanks muchly.
 