SocklessJ
Structural
- Aug 24, 2017
- 50
I have a single-story, steel-framed building with a 24' tall high roof. The exterior non-bearing stud wall has a brick veneer, and I'm wondering the best way to handle the deflection from wind.
Is it reasonable to put this all on the cold-formed delegated engineer? Per SSMA, this could work with an 800S200-68 GR50 studs @12" OC. However, I'm not sure if this will be seen as unreasonable and too costly.
I could add an HSS8x8 flush girt to break up the span, but I expect the architect won't like the aesthetics of having to box it out with drywall.
I could add a bypass girt in the plane of the studs, but I'll still need an HSS8x8 due to the 26' bay spacing. So my studs would also need to be 8" deep perhaps negating the cost savings.
How would you handle this situation? Most of my experience is with industrial structures, so interfacing with CFS is new to me.
Is it reasonable to put this all on the cold-formed delegated engineer? Per SSMA, this could work with an 800S200-68 GR50 studs @12" OC. However, I'm not sure if this will be seen as unreasonable and too costly.
I could add an HSS8x8 flush girt to break up the span, but I expect the architect won't like the aesthetics of having to box it out with drywall.
I could add a bypass girt in the plane of the studs, but I'll still need an HSS8x8 due to the 26' bay spacing. So my studs would also need to be 8" deep perhaps negating the cost savings.
How would you handle this situation? Most of my experience is with industrial structures, so interfacing with CFS is new to me.