I have 45' tall 12 cmu wall. This wall supports a roof and stage rigging system. The loads I have calculated are:
Dead Load - 1000 plf
Roof Load - 1000 plf
Live Load - 1620 plf (for the stage rigging equip.)
Wind Load - 17 psf
I have determined the wall should be reinforced with #6 at 16" on center, each face. The wall has brick veneer which I will support with a relief angle at 30'.
The deflection meets L/600 without the 0.7 reduction factor.
I am using the NCMA design software.
I have never designed a load bearing wall this tall before, so any thoughts would be greatly appreciated.
Thanks,
J