My question relates to ASCE 7 Chapter 15, particularly 15.7.5. I am designing the anchorage for a saddle supported liquid storage tank. Section 15.7.5 makes it clear that the overstrength factor is NOT to be used for tank anchorage calculations, because they are trying to force a ductile yield in the anchor, requiring the concrete to develop the full steel strength of the anchors in tension. However, do I apply the overstrength factor in my overturning calculations? When I do not use overstrength, there is no net overturning in the tank, i.e. no anchor tension. But, if I do use overstrength, there is a net overturning moment, so I get anchor tension. How would you approach this situation:
a) Do not apply overstrength to overturning calculations, no anchor tension, so shear governs anchor design. But, still apply the detailing requirements of 15.7.5 to design the embedment to develop the full strength of the anchor in tension, and provide 8*diameter of gauge length?
b) Do not apply overstrength to overturning calculation, no anchor tension, so shear governs anchor design, and do not apply the tension detailing requirements of 15.7.5.
c) Apply overstrength to overturning calculations, determining that there is tension in the anchor. Then, anchors would be designed for the governing tension/shear combination, and the detail requirements of 15.7.5.
On a side note, to accomplish the 8 diameter gauge length requirement, we would have to weld on a plate and pipe sleeve to give the anchor standoff above the concrete. The sub who is ordering the tank told me he has seen this detail before, but usually on vertical tanks, not horizontal like this one. So, maybe others have not used that requirement on this type of tank in the past. But, since all installations are site specific, and this is in a SDC D region, I want to determine for myself if this is actually required.
Thanks for any responses.
a) Do not apply overstrength to overturning calculations, no anchor tension, so shear governs anchor design. But, still apply the detailing requirements of 15.7.5 to design the embedment to develop the full strength of the anchor in tension, and provide 8*diameter of gauge length?
b) Do not apply overstrength to overturning calculation, no anchor tension, so shear governs anchor design, and do not apply the tension detailing requirements of 15.7.5.
c) Apply overstrength to overturning calculations, determining that there is tension in the anchor. Then, anchors would be designed for the governing tension/shear combination, and the detail requirements of 15.7.5.
On a side note, to accomplish the 8 diameter gauge length requirement, we would have to weld on a plate and pipe sleeve to give the anchor standoff above the concrete. The sub who is ordering the tank told me he has seen this detail before, but usually on vertical tanks, not horizontal like this one. So, maybe others have not used that requirement on this type of tank in the past. But, since all installations are site specific, and this is in a SDC D region, I want to determine for myself if this is actually required.
Thanks for any responses.