Is it reasonable to nitrogen blanket a tank at 1" W.C. ?
It seems tight with 1" set on control valve and 1/2" on conservation vent. And these aren't fancy Ostand blanketing / venting valves.
40' x 25' tank with flammable liquid.
Does barometric pressure play into this? I.E. if I set the valve on a low barometer day to 1" W.C. above atomospheric, and the next day the barometer jumps up, am I no longer 1" above atmospheric?