oneintheeye
Structural
- Nov 20, 2007
- 440
this may be a mouth full but here goes.
Your designing a tank, smallish size. Using plastic soil conditions.
The tank imposes a surcharge on the soil.
For the structural design you would tank the weight of walls spread over the base area which say produces a pressure of 15 kn/m2 (again just pulling figures out of air).
Therefore the pressure is applied over slab area and forces calculated.
Now if the water table rises above base and provides uplift of 10kn/m2.
Now is the pressure used to calculate forces 10 + 15 or 15 as the water buoyancy takes some of the pressure off soil.
Or two load cases. 1) wall weight over slab 2) force due to uplift of water.
For a continuous base and wall things will get more detailed.
So how would people approach? I'm having doubts i do it the most economical and no one seems too convinced here.
Your designing a tank, smallish size. Using plastic soil conditions.
The tank imposes a surcharge on the soil.
For the structural design you would tank the weight of walls spread over the base area which say produces a pressure of 15 kn/m2 (again just pulling figures out of air).
Therefore the pressure is applied over slab area and forces calculated.
Now if the water table rises above base and provides uplift of 10kn/m2.
Now is the pressure used to calculate forces 10 + 15 or 15 as the water buoyancy takes some of the pressure off soil.
Or two load cases. 1) wall weight over slab 2) force due to uplift of water.
For a continuous base and wall things will get more detailed.
So how would people approach? I'm having doubts i do it the most economical and no one seems too convinced here.