I would like to know your opinions or recomendations of the following case:
A 70 ft diameter by 32 ft Height API 650 Oil Storage Tank builded in 1995 suffered overpressure and crack on the roof to shell joint. After an ispection the damage reported was:
-6 out of 25 Shell plates had distortions. (See attatched picture)
- Most of the self supported roof U beams fell off or were deformed, approximately 70 % of its diameter were damaged and the main central column showed displacement.
- High level of Corrosion were detected on the annular ring
- Instrumentation were found OK ( Opening vent , relief valves, level meter)
After Reviewing API 650 , API 653 and API 2000.
The decision:
-Replacement of the entire roof and supports, includes: U beams, roof plates , central column.
-Replacement of the 6 distorted shell plates.
-Reinforcement of the annular ring and a medium or small percentage (will be determine by MPI an LP) of the remaing floor plates and welds.
-Shell plates are going to be cut on the weld since the whole plate is replaced
-Openings on the existing shell plates and roof plates are going to be build from scratch following AS-BUILT Drawings.
Note:
-Replacemente and repairs include Testing , calibrating , Maintenance, painting and procedures following the AS-BUILT design and drawings.
-Currently the tank is working with a very low level just enough to avoid pumps from cavitate
A 70 ft diameter by 32 ft Height API 650 Oil Storage Tank builded in 1995 suffered overpressure and crack on the roof to shell joint. After an ispection the damage reported was:
-6 out of 25 Shell plates had distortions. (See attatched picture)
- Most of the self supported roof U beams fell off or were deformed, approximately 70 % of its diameter were damaged and the main central column showed displacement.
- High level of Corrosion were detected on the annular ring
- Instrumentation were found OK ( Opening vent , relief valves, level meter)
After Reviewing API 650 , API 653 and API 2000.
The decision:
-Replacement of the entire roof and supports, includes: U beams, roof plates , central column.
-Replacement of the 6 distorted shell plates.
-Reinforcement of the annular ring and a medium or small percentage (will be determine by MPI an LP) of the remaing floor plates and welds.
-Shell plates are going to be cut on the weld since the whole plate is replaced
-Openings on the existing shell plates and roof plates are going to be build from scratch following AS-BUILT Drawings.
Note:
-Replacemente and repairs include Testing , calibrating , Maintenance, painting and procedures following the AS-BUILT design and drawings.
-Currently the tank is working with a very low level just enough to avoid pumps from cavitate