Tappered Round Columns 2

Status
Not open for further replies.

Greatone76

Structural
Feb 2, 2006
64
I am working with steel street light poles. They are a round section that tapers down from a larger section at the bottom to a smaller section at the top.

For the overall compression capacity, we use the entire height of the columns and we use the properties of the pole at the mid-height of the pole. Since these are tall slender members Euler Buckling of the overall member is what is going to control the design, the slenderness/capacity is highly dependant on the height of the member and radius of gyration.

We use the mid-height radius of gyration based on the AASHTO LRFD Specifications for Structural Supports for Highway Signs, Luminaires, and Traffic Signals (2015 version). C5.10.2.1 - says that using the radius of gyration at a distance of 0.50L is conservative for all tapered light poles.

For one particular example, I'm working with I get a compression capacity of around 2000 lbs for the pole. When I use that value and put it in the combined forces equation I have the pole as 1.2 utilization and have requested that my client utilize the next thicker pole gauge.

The pole manufacturer is pushing back and saying that utilizing the client's custom equipment on the pole that the currently proposed pole is acceptable. With that fact I requested the calculations in order to understand where they were getting their values and where our differences were.

Upon review of their calculations, I saw that we agreed on moment capacity, shear capacity, and torsion capacity, but their compression capacity was much larger than mine. Upon detailed review, it turned out that they were using a much larger radius of gyration nearer to the base of the column to get their compression capacity. Their capacity was around 7000 lbs. So they had utilization of 97%.

I wrote back to my client and informed them where I see the difference between my calcs and theirs and said while I understand that my mid-height radius of gyration may be conservative and I could justify a different value if they would provide an engineering reference I would be happy to adjust mine upward to match theirs and would change my calcs to agree if they could provide a reasonable reference for the higher radius of gyration value.

The manufacturer responded back that they divide the pole up into sections and check the capacity at the base of these different sections vs the loads. And for compression capacity, they use the properties at the bottom of the section and the height from the bottom of the section to the top of the pole. So at the mid-height, they use the radius of gyration at the mid-height and the height of the pole as half the height of the overall pole. So at the bottom, they confirmed they use the base radius of gyration and the whole height of the pole. Which I believe is not acceptable. To me, this would assume the whole height the column is buckling over is the largest section at the base transferred all the way to the top.

Question A - Am I correct in my thinking that using the base radius of gyration is completely inappropriate? Am I missing something about the pole being cantilevered from the base (fixed base fee top) and due to the shape the buckling happens mostly at the base, so the is appropriate?

Question B - Does anyone have a reasonable engineering reference where I can better utilize the 2/3 point of some other situation to get a reasonable higher value of the radius of gyration for a tapered round pole?

Question C - Any advice on how to handle the situation when communicating back to the client and manufacturer?
 
Replies continue below

Recommended for you

If we are addressing the critical buckling load of the column, the ratio of bending to axial load is irrelevant. The column, throughout its height, is less stiff than the base of the column, so Pcritical for the tapered column must be less than that of a column with constant base cross section throughout its height.

BA
 
The current AASHTO spec is based on the NCHRP Report 796. This report also included example calcs as an appendix (appendix C), which can be download here (also attached):

Example 3 covers what you are discussing. In this example, the radius of gyration at midpoint of the pole is used to find the slenderness ratio, KL/r for determining B2 per section 4.8.1 of AASHTO. However, on page 114 it uses the radius of gyration at the bottom of the pole for determining the axial capacity of the pole as far as I can tell.

*Edit*
Actually example 7 is probably closer as it is a round street light. The same uses of different radius of gyration as mentioned above are used however.
 
This has already been said, but I will repeat it:

Flexural (Euler) buckling of a column involves the entire member length. It is not a local buckling phenomena, and thus, the change of 2nd moment of area along the member length must be considered in calculations. A conservative way to simplify the setting is to calculate the column buckling using the weakest cross-sectional properties, i.e., the narrowest part of the column.

A very simple method to estimate the buckling capacity of any cantilever is to use Rayleigh-Ritz method, which allows incorporating both a variable 2nd moment of area and Young´s modulus.

- Assume a kinematically admissible displacement function ( w(x)= A*(1-cos(pi*x/L)) comes to mind, where A=constant)
- Calculate the strain energy stored in the beam at the point of bifurcation (eigenvalue) buckling [ d_Internal = 1/2 * integral(0-->L) E*I(x)*((w(x)´´)^2) dx where I(x) = 2nd moment of area as function of length (linear, parabolic or whatever else) and ´´ = 2nd derivative with respect to "x" ]
- calculate the energy of the external load [ d_P= -1/2 * P * Integral(0->L) (w´(x))^2 dx ].

Then, evaluate the integrals and set total potential energy equal to zero (dPI = d_Internal + d_P), take derivative with respect to unknown variable (in this example: "A"), and solve the buckling load "P".

You may google "rayleigh ritz cantilever buckling" or read up on your stability textbooks.

 
Dauwerda:

Axial capacity (by which I assume you refer to a simple normal stress calculation) must be performed at the weakest cross-section of the pole, assuming that the loading is a tip load (force = constant) at the cantilever free end. The reason for this is basic structural mechanics: stress = force/area.

Self-weight checks can be done using the bottom of the pole if the bottom of the pole has a larger cross-section than the free end of the pole, but such checks are usually not needed: pole self-weight is almost always negligible.
 
BART: Do you have a more clear copy of the Numeric method?

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
Dik said:
BART: Do you have a more clear copy of the Numeric method?

I believe Newmark's published example is merely the most well know use of that same "Method of Successive Approximations" that I brought up.

FWIW, I tried to find the Excel spreadsheet I did to validate the method of successive approximations. But, I didn't have any luck. I'm sure the file existed on my computer at RISA some years ago. But, it's lost to the me now.
 
Thanks, Josh...

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
Found it... downloaded from:

thread507-468568

thanks.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
dik said:
BART: Do you have a more clear copy of the Numeric method?

Yes, dik. It is included in "Contributions by Others" in Publications by SlideRuleEra entitled:
Notes on Newmarks's Numerical Procedures (25 Pages, 2.4 MB, .pdf)


BA
 
Thanks, BART

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 