ALK2415

Structural
Sep 15, 2014
279
0
16
IQ
Dear Friends
i have storage water tank structure [serve as building roof and storage tank]
for concrete slab structure (span 16 meters) applied loading 20+22 KPa [kN/m2]
1- my assumed slab depth is L/18 ---> H=16e3/18 =900 mm (DL = 22 KPa)
if i switch to prestressed slab
2- what will be the slab depth [approximate] ?
3- Is prestressed double Tee would be more cost effective option ?
 
Replies continue below

Recommended for you

hokie66 said:
If you posttension it, make sure it is bonded posttenioning.

Agreed. That's what I had intended to convey in my sketch when I referred to it as "grouted PT".

centondollar said:
How is it done skillfully?

1) Dial in your PT load balancing such that upwards vertical seismic effects either do not exceed residual dead loads or exceed them by a manageable margin.

2) Provide bonded top reinforcement to deal with any excess tensile stress generated by the exercise described in #1.

centondollar said:
...cause excessive cracking and that coupled with tendon shape (compression on the "wrong" side during a seismic event) would undoubtedly cause a risk for ULS failure in bending. Excessive amounts of top flange reinforcement would also be needed to resist the seismic hogging moment.

Presently, we have complete control over our cross sections, our levels of prestressing, the disposition of our prestressing, and our mild reinforcing. In the hands of a skilled designer, there's no reason for anything to be "excessive" or "undoubtably a risk for failure". All of this stuff is just the meat and potatoes a robust design effort.

centondollar said:
If extra rebar and cracking along the entire T-beam isn´t a problem, I guess it could be done.

I'd have bonded temperature and shrinkage reinforcement in the tee / ribbed slab flanges to begin with and, often, I suspect that would be enough on its own. If not, toss in an extra bar or pre-stressing strand in the top flanges.

With regard to cracking:

a) Again, this is something that is largely within the control of the designer and;

b) If a ULS level earthquake causes some cracking... boo frickin' hoo.

Prestressed, precast concrete is used in high seismic designs all the time. There are nuances associated with that, to be sure, but it's something that we already know how to do rather well.

c01_mmdwd0.png


c02_mpwypd.png
 
"1) Dial in your PT load balancing such that upwards vertical seismic effects either do not exceed residual dead loads or exceed them by a manageable margin.

2) Provide bonded top reinforcement to deal with any excess tensile stress generated by the exercise described in #1."
What do you mean by 1)? PT can only balance dead load and a minor amount of live load (anything else causes too much precamber and tension of top of section due to prestress), so I don´t see how it could be calibrated for large earthquakes. Once you choose a layout, you´re stuck with it.

"With regard to cracking:

a) Again, this is something that is largely within the control of the designer and;

b) If a ULS level earthquake causes some cracking... boo frickin' hoo.
"
You cannot really control the amount of cracking in a seismic event, if by "control" you mean "estimate with reasonable accuracy beforehand". Furthermore, if the structure has critical deflection limits (most structures do), the deflection post-earthquake will be excessive, since one of the main selling points of prestress is to provide predictable elastic stiffness. One may as well use a steel girder or truss if that elastic stiffness is lost during more or less minor earthquakes.

These are my spontaneous thoughts. If I ever have the time, I will skim the books you cited and maybe learn something not so obvious about this topic.
 
centondollar said:
What do you mean by 1)? PT can only balance dead load and a minor amount of live load (anything else causes too much precamber and tension of top of section due to prestress), so I don´t see how it could be calibrated for large earthquakes. Once you choose a layout, you´re stuck with it.

You've got two things causing potential uplift on the system:

1) The vertical seismic loads which tend to be relatively small, even when the horizontal seismic loads are large. [V = 0.2 H_short_period] or something like that.

2) The balancing effect of the prestressing if it is draped to produce that effect.

Yes, if those two effects combine to snap the concrete in tension where it would normally be in compression under gravity loads, that is a potential problem. However, I submit that designer can solve that problem by:

A) Adjusting the balancing force -- drape and prestress -- such that no net uplift occurs, even under the expected seismic demand and/or.

B) Providing bonded reinforcing in the areas where the flexural stress reversal is anticipated.

Prosecuting strategy [A] will likely reduce the efficacy of the prestressing relative to situations where that constraint is not present. And, for that matter, so will a high ratio of live to dead load as hawkaz intimated earlier with respect to designing for the "empty". Will these reductions in efficacy alter the project economics such that prestressing is no longer a viable strategy? I don't know. For me, finding out would be the exercise of "design" in this situation.

centondollar said:
You cannot really control the amount of cracking in a seismic event..

I believe that you can:

1) If you wanted to badly enough, you could introduce enough P/A into the concrete such that it would not crack at all under the anticipated seismic demand.

2) You can provide bonded reinforcing designed to limit crack widths.

Naturally, since there is a lot of uncertainty involved in estimating seismic demands, there is also a lot of uncertainty involved in estimating seismic crack widths. Welcome to seismic design. The salient thing to recognize here, I feel, is that it is within the designer's power to design a prestressed concrete structure that satisfies whatever crack control limits would normally be imposed upon a non-prestressed structure. As such, the potential for cracking ought not be viewed as something that automatically renders a prestressed concrete structure unviable.

centondollar said:
Furthermore, if the structure has critical deflection limits (most structures do), the deflection post-earthquake will be excessive, since one of the main selling points of prestress is to provide predictable elastic stiffness. One may as well use a steel girder or truss if that elastic stiffness is lost during more or less minor earthquakes.

I disagree and feel that, with the bolded statement above, you are again imposing a binary, go/no-go judgment upon the viability of a system that is within the designer's power to control. The post-earthquake deflection of the beams will only be "excessive" if the designer allows it to be excessive. If desired, a designer could readily:

a) Design prestressed beams that do not crack during minor seismic events and, thus, retain their full, elastic-ish stiffness. Stuff like this is the meat of the Performance Based Design approach.

b) Design prestressed beams that possess sufficient stiffness even after they crack flexurally during a seismic event.
 