marinaman
Structural
- Mar 28, 2009
- 195
How do you guys distribute temperature and shrinkage reinforcment in thick machine slabs?
For example, I've got a machine slab that is about 60' long, 2' thick, and about 12' wide. I've completed all the analysis for the loads from the machine on to the mat foundation, including the use of soil perameters from the soils report we developed specifically for this machine foundation.
ACI Chapter 7 states that my minimum temp and shrinkage reinforcment should be 0.0018 times the area....or...about (24") x (12") x (0.0018) for about 0.5184 square inches per foot width.....each direction.
Per analysis (not including temp and shrink), I've determined I need about (1) #6 bar at 12" o.c., each direction, each face. That gives me about 0.44 square inches of steel, each direction, each face.....and....about 0.88 square inches per foot width.
My question is.....does ACI chapter 7's minimum reinforcing steel number of about 0.5184 square inches per foot width mean that I need that much per face of slab......or just I need that much steel across the section (in other words, I could've used, for temp and shrinkage, (1) #5 bar in each face and met the temp and shrinkage requirement per (2) x (0.31 square inches) = 0.62 square inches.
Just trying to be sure I don't need 0.5184 square inches per face (top AND bottom) each direction.
For example, I've got a machine slab that is about 60' long, 2' thick, and about 12' wide. I've completed all the analysis for the loads from the machine on to the mat foundation, including the use of soil perameters from the soils report we developed specifically for this machine foundation.
ACI Chapter 7 states that my minimum temp and shrinkage reinforcment should be 0.0018 times the area....or...about (24") x (12") x (0.0018) for about 0.5184 square inches per foot width.....each direction.
Per analysis (not including temp and shrink), I've determined I need about (1) #6 bar at 12" o.c., each direction, each face. That gives me about 0.44 square inches of steel, each direction, each face.....and....about 0.88 square inches per foot width.
My question is.....does ACI chapter 7's minimum reinforcing steel number of about 0.5184 square inches per foot width mean that I need that much per face of slab......or just I need that much steel across the section (in other words, I could've used, for temp and shrinkage, (1) #5 bar in each face and met the temp and shrinkage requirement per (2) x (0.31 square inches) = 0.62 square inches.
Just trying to be sure I don't need 0.5184 square inches per face (top AND bottom) each direction.