Per ACI 318-19, what is the difference between a "Combined Footing" per section 13.3.2 for 'One Way Shallow Foundations', versus a "Two-way combined footing" per section 13.3.4
The design provisions for one-way shallow foundations lead the user to Chapter 7 for one-way slab, which will require shrinkage and temperature reinforcing in the 90° direction.
However, Two-way combined footings send the user to Chapter 8, for the design of two way slabs, which does not have a minimum for shrinkage and temperature. I'm assuming here you don't have shrinkage reinforcing because you need to provide Asmin in each primary direction. (Which cannot be split between two faces anymore)
Also, for one-way shallow foundations per section 13.3.2:
13.3.2 One-way shallow foundations
13.3.2.1 The design and detailing of one-way shallow
foundations, including strip footings, combined footings,
and grade beams, shall be in accordance with this section
and the applicable provisions of Chapter 7 and Chapter 9.
Now, correct me if I'm wrong, but the intention here is to send the user to Chapter 7 (One Way Slabs) for strip footings and combined footings ONLY.
For grade beams, the user will go to Chapter 8 (Beams)? The reason I say this is grade beams don't require min. shrinkage and temperature reinforcing in the 90° direction, but combined footings should have this.
It also looks like we're no longer allowed to split the Asmin reinforcing between two faces for combined footings.
R7.6—Reinforcement limits
R7.6.1 Minimum flexural reinforcement in nonprestressed slabs
R7.6.1.1 The required area of deformed or welded wire
reinforcement used as minimum flexural reinforcement
is the same as provided for shrinkage and temperature in
24.4.3.2. [highlight #FCE94F]However, whereas shrinkage and temperature reinforcement
is permitted to be distributed between the two
faces of the slab as deemed appropriate for specific conditions,
minimum flexural reinforcement should be placed as
close as practicable to the face of the concrete in tension due[/highlight]
to applied loads.
The design provisions for one-way shallow foundations lead the user to Chapter 7 for one-way slab, which will require shrinkage and temperature reinforcing in the 90° direction.
However, Two-way combined footings send the user to Chapter 8, for the design of two way slabs, which does not have a minimum for shrinkage and temperature. I'm assuming here you don't have shrinkage reinforcing because you need to provide Asmin in each primary direction. (Which cannot be split between two faces anymore)
Also, for one-way shallow foundations per section 13.3.2:
13.3.2 One-way shallow foundations
13.3.2.1 The design and detailing of one-way shallow
foundations, including strip footings, combined footings,
and grade beams, shall be in accordance with this section
and the applicable provisions of Chapter 7 and Chapter 9.
Now, correct me if I'm wrong, but the intention here is to send the user to Chapter 7 (One Way Slabs) for strip footings and combined footings ONLY.
For grade beams, the user will go to Chapter 8 (Beams)? The reason I say this is grade beams don't require min. shrinkage and temperature reinforcing in the 90° direction, but combined footings should have this.
It also looks like we're no longer allowed to split the Asmin reinforcing between two faces for combined footings.
R7.6—Reinforcement limits
R7.6.1 Minimum flexural reinforcement in nonprestressed slabs
R7.6.1.1 The required area of deformed or welded wire
reinforcement used as minimum flexural reinforcement
is the same as provided for shrinkage and temperature in
24.4.3.2. [highlight #FCE94F]However, whereas shrinkage and temperature reinforcement
is permitted to be distributed between the two
faces of the slab as deemed appropriate for specific conditions,
minimum flexural reinforcement should be placed as
close as practicable to the face of the concrete in tension due[/highlight]
to applied loads.