Dear all;
If you had to purchase a new generator, - 400 MW, H2 inner cooled - what is the maximum temperature that you would expect to measure at full load? For the windings, assuming class F, in theory you could accept 155 ºC - 15 ºC for hot spot tolerance = 140 ºC... but I have never seen any generator running hotter than 90 ºC as measured by RTD. On the other hand, what would be a safe level of temperature to have in the core, especially in the end of the core, when absorbing reactive power? Are you aware of standards that give values for this? Any ideas will be appreciated.
If you had to purchase a new generator, - 400 MW, H2 inner cooled - what is the maximum temperature that you would expect to measure at full load? For the windings, assuming class F, in theory you could accept 155 ºC - 15 ºC for hot spot tolerance = 140 ºC... but I have never seen any generator running hotter than 90 ºC as measured by RTD. On the other hand, what would be a safe level of temperature to have in the core, especially in the end of the core, when absorbing reactive power? Are you aware of standards that give values for this? Any ideas will be appreciated.