I'm working in a power station where the ambient temperature is close to 55 deg C.What derating factor could be used for the loading of the generators? I know that the best way to obtain the derating factor is from the supplier but the generators are very old stuffs and I'm looking for a reasonable factor.I presume a ten degree rise in working temperature is considerable.The generators are of 5000 kVA size.

Guardiano
 
Replies continue below

Recommended for you

That's very hot. Does the generator nameplate give an ambient temperature for the rating? Normally it would be 40 deg C.

Is the generator air-cooled?

David Castor
 
Assuming that the old windings are of class B insulation, 120 degrees C would be the maximum operating temperature according to most standards. Therefore, at 40 degrees C ambient the permissible temperature rise would be 80 K. If the ambient temperature is 55 degrees C, then the maximum operating temperature still is 120 degrees C but the permissible temperature rise would be 65 K only. Make sure that site elevation is less than 1000 metres above sea level, otherwise the temperatures mentioned above have to be reduced.

Wolf
 
Yes, wolf39 is right. The deciding point is not the ambient temperature but the total temperature (ambient + rise). The generator's insulation temperature rise and temperature class is the deciding factor. This information should be provided on the nameplate for larger generators.

I agree with wolf39 that you will probably find that you have a Class B insulation which allows a stator temperature of 120C. This corresponds to 40C ambient + 80C rise.

If you have RTD's (dpc's question) then you can determine if your generator is running too hot.
 