In your opinion under the following condtions would large motors 300 kw to 4000 kw be able to copewith the following
"Motors shall be capable of recovering normal operation in the event of a system disturbance causing temporary loss of supply voltage of periodfs of upto 0.2 seconds ( fault clearance time ) followed by a sudden restoration, intially to 60% rated voltage for 3 seconds, then followed by a sudden restoration to 80% voltage, from which voltage the motors shall then be capable of accelerating and ulitmate recovery under the most arduous conditions. )Pump full load, open discharge )"
Your thoughs would be welcome, thanks
"Motors shall be capable of recovering normal operation in the event of a system disturbance causing temporary loss of supply voltage of periodfs of upto 0.2 seconds ( fault clearance time ) followed by a sudden restoration, intially to 60% rated voltage for 3 seconds, then followed by a sudden restoration to 80% voltage, from which voltage the motors shall then be capable of accelerating and ulitmate recovery under the most arduous conditions. )Pump full load, open discharge )"