Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Temporary power drop discussion 3

Status
Not open for further replies.

itsmoked

Electrical
Feb 18, 2005
19,114
I have a big generator that's costing $8,100/mo to rent.
$150/mo fee for the CA air quality board.
$4,400/mo fuel.

Waiting for the new power drop from the POCO will take at least 8~9 months.

We're searching for a solution to the $12,650/mo pain.
The generator panel has never shown more than 50A @ 480V.

I have a power pole field drop with 200A 240V delta service barely used, a couple of lights.
One way distance is 750ft.
I have a 240/480 50kVA transformer.
2 AWG will cause a 2% drop carrying 50A.

My biggest concern is motor starting. I don't yet know what the largest motor is that needs to be supported. From memory I don't think there's probably one bigger than 15hp/480v but I'll have to check later today.

What do you think, doable?

If you think this can work, do you have any suggestions for 'cheap' cable or wire? This is all temporary.


Keith Cress
kcress -
 
Replies continue below

Recommended for you

If the cable has a J in the type, it is only rated for 300 volts.
 
Sorry for doubting you on that Keith.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor