Good day everyone,

I'm not really one to take shoring jobs but a friend of mine asked, so I am entertaining the request. FWIW I am 90% focused on residential, custom home design and maintenance engineering.

Situation:

Commercial building, three storeys above grade. Block walls (CMU) above grade, poured foundation wall. 14" OWSJ at 24" o/c throughout the building bearing onto steel columns and beams. Pretty typical as far as structural detailing goes. There was a fire on the second floor of the building; the fire was confined to one bay of the building. The investigation (by other eng consultants) found damage to all joists and steel decking in the ceiling space above the fire-affected region. As a consequence that area of the third-floor sagged and needs repairs. These repairs are already detailed and can be seen in the attached snippet ("Affected Area").

Affected_Area_pblwzj.png


The repair details, provided by others, are shown here ("Repairs"):

Repairs_qececo.png


Thoughts:

My friend, who is the restoration contractor, is asking for shoring details because the repair drawings have a boilerplate note indicating "shoring details by others". Looking at the plans I actually don't seen much shoring being required but I want to pick your brains nonetheless. The main elements carrying the loads (the W360x72 beam, the W360x33 steel beam, the supporting steel columns, and CMU walls) were found to be in good condition and didn't require removal. The CMU walls need some repairs but the scope is fairly minor.

The third storey's steel deck is going to be cut out, removed, and replaced along with the affected OWSJs in sections. Since the beam carrying the majority of the OWSJ loads (the W360x72) is remaining and is OK in condition, I'm a touch worried that I am missing something here. Or is it as simple/plain-Jane as it appears to me? The layout of the third floor, above, is identical to the the second floor and there are no point loads landing anywhere in the affected region. Thoughts?
 
Replies continue below

Recommended for you

I'd tend to agree with you given the information at hand. But I may not have the whole story. Perhaps removing that section of floor will have consequences for the vertical element stability until the deck is reinstated and concrete poured. Maybe not.

I have however come across situations before where the EOR has just boiler plated the "shoring as required by others" and it turned out that nothing was required. But they still demanded a sealed letter from us confirming that no shoring was necessary to complete the construction.
 
Thanks @jayrod12, that is something that I've run into before as well. I am going to see it for myself in person this week so I will have a better understanding then. Thanks for the input.
 