TEDstruc
Civil/Environmental
- Dec 6, 2017
- 43
Application: Fully Pre-tensioned Bolts subject to tensile cyclical loads. I am looking specifically at AISC 360-10 today since that is the edition I have at the office (I have 360-15 at home), although I think 360-15 is similar.
Appendix 3, section 3.4, states "For joints in which the material within the grip is limited to steel and which are tensioned to the requirements of Table J3.1 (Fully Pretensioned), an analysis of the relative stiffness of the connected parts and bolt shall be permitted to be used to determine the tensile stress range in the pretensioned bolts due to the total service live load...etc...."
However Table A-3.1, section 8.5 (the only section applicable to bolts in tension), applies only to non-pretensioned bolts.
Commentary on appendix 3, section C3.4 goes on to say that "Fatigue resistance of bolts subject to tension is predictable in the absence of pretension and prying action....etc....To limit the uncertainties regarding prying action on the fatigue of pretensioned bolts in details which introduce prying, the design stress range provided in Table A-3.1 is appropriate for extended cyclic loading only if the prying induced by the applied load is small." Okay.... I guess we should just size our connecting elements to eliminate all prying in this application...since there seems to be no indication on what "small" prying is...
RCSC Section 4.2 lists "Joints with ASTM A325 or F1852 bolts that are subject to tensile fatigue" under joint applications required to be fully pretensioned.
So to summarize, we are required to fully pretension the bolts, but the allowable stress range is only applicable for non-pretensioned fasteners, or fully pretensioned fasteners where the joints see only "small" prying.
Furthermore, What is the allowable total bolt tensile stress when bolts are fully pre-tensioned? For non-pretensioned, allowable stress is 45 ksi for A325 bolts, but a fully pretensioned bolt is pretensioned to about 64 ksi... so what is the allowable total tensile stress for a PT bolt? I understand that pretensioning reduces cyclic stress range if no prying is introduced, but the externally applied cyclic load is still stressing the bolt to some total stress value above the initial pretension stress....
Appendix 3, section 3.4, states "For joints in which the material within the grip is limited to steel and which are tensioned to the requirements of Table J3.1 (Fully Pretensioned), an analysis of the relative stiffness of the connected parts and bolt shall be permitted to be used to determine the tensile stress range in the pretensioned bolts due to the total service live load...etc...."
However Table A-3.1, section 8.5 (the only section applicable to bolts in tension), applies only to non-pretensioned bolts.
Commentary on appendix 3, section C3.4 goes on to say that "Fatigue resistance of bolts subject to tension is predictable in the absence of pretension and prying action....etc....To limit the uncertainties regarding prying action on the fatigue of pretensioned bolts in details which introduce prying, the design stress range provided in Table A-3.1 is appropriate for extended cyclic loading only if the prying induced by the applied load is small." Okay.... I guess we should just size our connecting elements to eliminate all prying in this application...since there seems to be no indication on what "small" prying is...
RCSC Section 4.2 lists "Joints with ASTM A325 or F1852 bolts that are subject to tensile fatigue" under joint applications required to be fully pretensioned.
So to summarize, we are required to fully pretension the bolts, but the allowable stress range is only applicable for non-pretensioned fasteners, or fully pretensioned fasteners where the joints see only "small" prying.
Furthermore, What is the allowable total bolt tensile stress when bolts are fully pre-tensioned? For non-pretensioned, allowable stress is 45 ksi for A325 bolts, but a fully pretensioned bolt is pretensioned to about 64 ksi... so what is the allowable total tensile stress for a PT bolt? I understand that pretensioning reduces cyclic stress range if no prying is introduced, but the externally applied cyclic load is still stressing the bolt to some total stress value above the initial pretension stress....