I am workng on an addition that has three walls being added to an existing structure. Do the layout of the roof framing plan I am not able to tie in the addition to the existing structure. I looked at the building as a three-sided diaphragm via a Vulcraft publication that I have. My question is, can I use a bar joist to develop the diaphragm tension/compression load for the open end? I have put a call into Vulcraft but I have not heard back yet. I am exploring this as an option.
 
Replies continue below

Recommended for you

You must be referring to lateral loads acting perpendicular to the open side of the diaphragm, since for loads parallel there isn't a chord.

The answer to your question is yes. If the chord force is significant, you should put a note on the drawings instructing the joist supplier to design for the force. But I have found the chord force due to D + 0.75L + 0.75W (or 0.75*0.7E) is usually less than the chord force due to D + L.

DaveAtkins
 
How do you get a chord force in a diaphragm for D+L?
 
I can see how my response is confusing.

In the first paragraph of my response, I was referring to the diaphragm chord.

In the second paragraph of my response, I was referring to the top chord of the joist which is acting as the diaphragm chord.

DaveAtkins
 
I can see your point about the forces being less, but the D+L will put a compression force in the top joist chord and the lateral load would either add a tension force, reducing the D+L compression force or add a compression force, depending on which direction the lateral force is applied. Correct?

Would also think that the D only due to gravity should be checked with the two lateral load conditions.
 
Correct. But I still think you need to consider roof live load or snow load in combination with lateral load--check the applicable Code to be sure.

DaveAtkins
 