tension field action plate girder- latest code

Status
Not open for further replies.

rfied112

Structural
Oct 16, 2003
10
Regarding plate girder design with stiffeners, previously to be allowed tension field action the panel aspect ratio a/h had to be less than 3.0 and the codes listed an 'arbitrary" fabrication handling suggestion of aspect ratio< 260/ (h/t)2.

AISC 2005 Commentary G4 now defines the 260/ (h/t)2 as MANDATORY to allow tension field action. Anyone have any ideas on this discrepancy???
 
Replies continue below

Recommended for you

rfied112 - where in the 3rd edition did it state that the ratio was a suggestion - in G3 it is a specific requirement. This specific requirement is carried over into the 13eth edition in G3.1(b).
 