I don't follow. For tensile rupture, you get a capacity of 0.5*Fu*U*A. For your shape and A36 material, Fu is 58 ksi, U is 0.9, so you get a maximum stress of 26.1 ksi on the gross area.Have a look at the equation for tension rupture. Assume a channel (MC shape, say 6") bolted with (8) 3/4" A325 bolts in one line. Assume a bolted connection and a shear lag factor of 0.9 (code limitation). Now do something silly and calculate the hole area based upon a diameter of zero. Calculate the allowable load and put it aside. Now check the same channel for tension on the gross section. With the bolt hole area at zero inches squared, tension rupture controls.
It doesn't typically control for A36 material, maybe, where there is a larger difference between Fy and Fu. It's controlling for your material, whether you use ASD or LRFD, because Fy and Fu are much closer to each other.It doesn't typically control in ASD so you can understand the lack of photos.