there is a terminal bock inside lighting junction box EEx'e' installing in Hazardous area.
I need to know that require pin lug for cable connection in this terminal blocks or not?
And If without pin lug what will happen when energise.
Note this terminal block is screw type,
thanks
 
Replies continue below

Recommended for you

For a solid (unstranded) conductor you do not need a lug. For stranded conductors you need a lug.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Since your JB is already explosion proof, the termination will be same as insafe area. Check the type of terminal block and apply the compatible terminal lug. Scotty is correct, you need not to connect terminal lug on single conductor.
 
Jed057,
Your box is EEx"e" type which means "increased safety" design.Therefore,the terminal block has got extra creepage distances to avoid sparks.Therefore,use normal lugs if it is a stranded conductor and wire normally.There cannot be special wiring methods.
 