Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Terzaghi’s Bearing Capacity Factor - Ng 1

Status
Not open for further replies.

mar2805

Structural
Dec 21, 2008
372
Hi folks!
When using standard formula for Kp (lateral passive earth pressure) in Terzaghi formula, I cannot get an correct value for N gamma.
Egsample for 30deg, N gamma should be 19,13.
Using equation attached I get an value of 0.866
Whats wrong?
 
Replies continue below

Recommended for you

I do not know where you obtained your formula for Ngamma, but the image is from terzaghi's book.
image_et7g6i.png
 
Hello, /i have a similar question for piles,is there a formula for Nq relating to friction angle in wet soil (sand) or we should refer to the graph only.. I need a formula of Nq function of friction angle for derivation and other purposes than usual bearing capacity calculation so that's why..
 
Status
Not open for further replies.

Part and Inventory Search