tpe1973
Structural
- Aug 15, 2007
- 2
I am working on a balloon framed, masonry veneer warehouse structure from around 1910 that the client would like to reuse as retail/office and residential space. My initial analysis using modern design strengths for the wood members indicated that quite a bit of strengthening would be required for the intended use.
The building is constructed of southern pine 2 x 12 joists and beams (beam is 4 laminated 2x12) with white oak 8 x 8 columns. All are planed to approximately modern dimensions. Visual inspection led me to believe that the wood was stronger than what modern code allows due to the density of the members and the overall stiffness of the floor system.
The owner was concerned about the cost of the originally proposed remediations and agreed to remove members to be tested. I had samples prepared and tested according to ASTM D143. Using the results from these tests, I calculated allowable loads considering defects (Grade of wood) and safety factor according to ASTM D245. The results I obtained were approximately 2-3 times higher than modern code allowable stresses. Now that I have these very high results I am reluctant to use them even though it seems that the AF&PA allows it.
Has anyone ever done something similar? Did I miss something in my analysis or are these indeed the loads I can use?
The building is constructed of southern pine 2 x 12 joists and beams (beam is 4 laminated 2x12) with white oak 8 x 8 columns. All are planed to approximately modern dimensions. Visual inspection led me to believe that the wood was stronger than what modern code allows due to the density of the members and the overall stiffness of the floor system.
The owner was concerned about the cost of the originally proposed remediations and agreed to remove members to be tested. I had samples prepared and tested according to ASTM D143. Using the results from these tests, I calculated allowable loads considering defects (Grade of wood) and safety factor according to ASTM D245. The results I obtained were approximately 2-3 times higher than modern code allowable stresses. Now that I have these very high results I am reluctant to use them even though it seems that the AF&PA allows it.
Has anyone ever done something similar? Did I miss something in my analysis or are these indeed the loads I can use?