Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Testing (Hydro) of a spare valve 1

Status
Not open for further replies.

ER_Azza

Mechanical
Jul 18, 2018
54
Hi All

Need a bit of opinion.
I've work at different companies and many have slightly different rules when it comes to using a spare valve (new or refurbished).

When a valve (out of storage) is to be used, it will need to undergo a hydro test if the last test was done on it more than a year ago.
Seems common in many industries. But I never found that requirement clause in the ASME Standard.
 
Replies continue below

Recommended for you

For us in the marine industry, a valve needs to tested prior to installation. The classification society will witness the test. Contact pattern or hydrostatic testing are acceptable.

I don't think ASME has jurisdiction here as they're mostly involved in the construction of the valve.
 
What type of valve are you discussing? Generally a hydro test would have already been done and certified by the original manufacturer. Why do it again? unless its design requires it.


*** Per ISO-4126, the generic term
'Safety Valve' is used regardless of application or design ***

*** 'Pressure-relief Valve' is the equivalent ASME/API term ***
 
This falls into the custom and practice part of life.

There is no real reason why this valve needs a hydro test unless someone has lost the previous test results.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
I suggest that the reason I would recommend testing a valve that has been in store for a period of time is that (often) valves are not stored particularly well and it is much better to find out that the valve is not working as it should BEFORE it is installed into line and NOT afterwards! The problem with hydrotesting is that it is not always possible to get all the test water out after testing, so residual test fluid will remain in the valve and, potentially, corrode sealing faces whilst it sits quietly in store, awaiting its time to shine. Indeed I suggest that with a trunnion mounted ball valve it is impossible to get all the test water out unless it is purged on dry gas or similar.

These days there are a lot of good preservation products on the market that can inhibit corrosion in the store, but they need to be applied correctly and maintained, and each of these aspects is as important as the other. Irrespective, I think that a quick pressure test prior to installation pays dividends.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor