I want to perform the High voltage test for 33kV power cable.

1. what is max. applied voltage in case of AC supply as well as DC supply?

2. which standard i have to refer?
 
Replies continue below

Recommended for you

If you are in Canada these standards may help:

CSA C68.3 Shielded and Concentric Neutral Power Cables Rated 5 - 46 kV

CSA C22.2 No. 0.3 Test Methods for Electrical Wires and Cables

Regards
 
Before you consider doing a DC hipot you should serch for threads here on that topic.
 
IEEE std 400.1 for dc
IEEE std 400.2 for VLF (very low frequency)

Also manufacturer recommendation are a good ressource as said before
 