Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

THD in 20 kV side of 20/0.4 kV Transformer, 3000 kVA, Dyn-5, Year 2019

Status
Not open for further replies.

JonoJakarta

Electrical
Jun 9, 2007
5
0
0
ID
Dear expert,

I found in THD our PM5500 meter on our SM6-24 switchboard showing around 50%-52%, I was surprised.
Is this coming from load side (LV/0.4 kV) or on HV side?
Then, I switch off ACB on LV side of Transformer , it's mean our transformer on no-load condition
I checked PM5500 meter on our SM6-24,there is showing THD still there but decrease to 45%-48%, current 689,86 mA, Voltage, 20.4 kV.
My question:

1. Why is there still THD on the HV side(20 kV) even though the LV side is off/no load?
2. What is caused?
3. Is the transformer on healthy condition?

Any comments are welcome.
Your prompt reply will be highly appreciated.

Thank you,
Best Regards,
Jono
 
Replies continue below

Recommended for you

Where is the current and voltage input to the 20kV side meter coming from? Traditional CTs and PTs? Do you know what their frequency response is?



 
Dear bacon4life,

THD in current

Dear Scottf

I think traditional CTs and PTs, There is not mention the manufacture but the data of CT's is :CT, 100-200/5-5A 16kA 30VA cl 0.5 7.5VA 5P15 and for PTs :VT, 15-20kV/V3:100V/V3;cl0.5 30-50VA.
About frequency response, i dont have information
 
I'm new to this forum so hope this goes thru.
You may want to connect a load on the LV side and then take your measurements. Try to avoid a n0n-linear load.
Open circuit (unloaded) readings of THD may be meaningless in your application.
 
Status
Not open for further replies.
Back
Top