the cooling water thermodynamic analysis used for cooling water chillers is
1TR=3.5KW= m CPw (twi-two)
m= 3.5 /(4.18 x (32-37))
= 0.167 kg/s
volume flow rate = 2.65 gpm
is that right?
cause i know that as a rule of thumb that 1 TR needs 3 gpm cooling water
1TR=3.5KW= m CPw (twi-two)
m= 3.5 /(4.18 x (32-37))
= 0.167 kg/s
volume flow rate = 2.65 gpm
is that right?
cause i know that as a rule of thumb that 1 TR needs 3 gpm cooling water