wiktor
Structural
- Apr 11, 2002
- 232
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Difficulties with the quarter-point detail in balanced cantilever construction led to another
construction approach to providing expansion joints in long structures of long span lengths.
This method calls for placing expansion joints over the piers and temporarily stressing the
expansion joint segments together to form a single pier segment. The segments on either side
of the expansion joint are then placed in cantilever until the adjacent mid-spans are reached.
Once closure joints are poured and continuity tendons stressed, the cantilever tendons through
the expansion joint segments are removed and the two expansion joint segments separated
from each other to allow the necessary thermal and long-term movements. This method of
construction was used at the Roosevelt Bridge in Martin County
I've found several photos online which I believe are of this bridge. (they aren't always labelled) It would seem that the space for bottom tendons is minimal so this bridge is largely a cantilever design. Though the end being discussed looks to be simple supported.LittleInch said:Anyone found any drawings of how they tied the box sections together?
LittleInch said:[/Only if they've found issues with the top tendons would the bridge be in serious danger.]
Any cracked tendon is a serious risk, and the excellent photograph you have posted clearly shows that one (or more) of the bottom (so called continuity) tendons has snapped, as the crack is wider at the bottom, indicating total loss of post tensioning in this area. As the transmission of the shear forces in between the segments relays on the "forced friction" and protrusions matching recesses in the adjoining element, it's a rather big problem. Also, having intact top tendons, and corroded bottom ones, is adding to the positive (LL) moments in the span.
Anyway, any transverse or vertical crack in post-tensioned structure is indication of a very serious problem, and any competent engineer would close such bridge immediately.