Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Thermal storage tank in chilled water system

Status
Not open for further replies.

Manu68

Mechanical
Nov 18, 2013
36
0
0
IN

Dear Experts,

In a closed loop chilled water system with chiller, primary and secondary pumps, we have a thermal storage tank that can store chilled water. The water in the tank is maintained at 6.7deg.C and when chiller is out of service, water stored in the thermal storage tank will be the pumped to the load (AHU, FCU etc) by the secondary pumps.

Since this thermal storage is part of the closed loop pressurized line, how can we provide air venting at the time of initial line filling and maintaining the tank at same pressure as the chilled water line is. Can you please throw some light on the ports (inlet outlet, air vent, over flow drain pipe etc.

Regards,
Manu
 
Replies continue below

Recommended for you

Status
Not open for further replies.
Back
Top