There are ways to calculate stresses due to temperature gradients and autogeneous and drying shrinkage (see e.g., CIRIA thermal cracking recommendations) and the reinforcement required to minimize cracking do to those effects. Tensile strain due to restraint at the wall-floor or wall-ground interface, can be found in e.g., Eurocode. Reinforce for that, close to the wall faces, and choose cement so it contains minimum Portland cement and significant amounts of slag - this reduces the peak curing temperature and therefore restricts cracking from temperature gradient between wall core and wall faces, but it also slows down strength development. The peak temperature during curing can be found in nomograms (function of wall thickness and mix type).
You may also consider casting in two layers (18 inches at a time) if you can't make it work in any other way. However, that would require stirrups or some other form of shear keys to connect the two wall segments, so it might not be economical.
PS. The dimensions of this wall are quite unusual. 3 meters tall and 0,9 meters thick (approximately) - what is it used for?