threaded rod allowable tensile stress

Status
Not open for further replies.

gte447f

Structural
Dec 1, 2008
799
I have seen 9000 psi used as an allowable tensile stress for threaded rod on several load tables from manufacturers, etc. Anyone know how this value was derived?
 
Replies continue below

Recommended for you

If you are using it for any critical structural application, get a mill certificate for the material. Threaded rod can come from anywhere and doesn't necessarily always comply with any particular standard.
 
Ron, I agree that they can come from anywhere. I think that is the reason for the overly conservative 9000 psi allowable stress that is sometimes referenced. I found a reference in a footnote to a hilti product data sheet to MSS SP-58 which states 12000 psi for AISI 1010 steel. Hilti aplies a further 25% reduction to "allow for normal installation and service conditions".
 
As you have already noticed, many of the pipe support manufactures seem to use 9 ksi for the allowable stress in threaded rods. Salmon and Johnson's Steel Structures Design and Behavior uses AISC 360-05 Section J.3 (bolted connections) to calculate the capacity of tension rods. When I want to justify more than 9 ksi for hanging equipment with A36 threaded rods, I treat it as a tension member (AISC 360 chapter D) and use the minor diameter of the threads to calculate the gross area.
 
I can't find any references to AISI 1010 in MSS-SP-58, but section 4.7 in the document specifies the 25% reduction that Hilti applied as you pointed out.

Several different factors can contribute to safety factors much greater than typical structural specifications:
- MSS-SP-58 (and presumably whatever Hilti product you're looking at) was specifically developed for pipe hangers and supports. Safety factors for mechanical applications tend be grossly over-conservative to account for fatigue and other accidental loading conditions, and
- AISI 1010 doesn't specify any particular strength but only the composition. Unless tested or specified, the steel MAY have different properties/strength variabilities than A36 or A992.