In a grid system, distribution system is fed from 132/11Kv star/star solidly grounded system.11Kv system feed to loads through 3 phase 3 limbed core type distribution transformers of delta/solidly grounded star connection.Now the utility plans to use 3 single phase shell type (wound core ) transformers to get 3 phase solidly grounded star/grounded star connection.Of course this secondary load will be isolated from former loads to take care of phase shift.Any problem in this application? Any special precautions to be taken?
 
Replies continue below

Recommended for you

I don't think will be any difference. If the impedance is different, you may need to review protection.
 
Definitely, you need to review your relay coordination, since the delta was a filter to the high side world of zero sequence faults (L-G or LL-G) on the star side, but if now you are going to have star-star solidly grounded on both sides, you are going to have a path for this currents, and threfore, you need to coordinate the ground relays.

Good luck!

 
What sanchexjl said. Your zero-sequence relaying will need to be reevaluated.
 