rhpope
Mechanical
- Mar 3, 2006
- 16
This is related to the previous thread from yesterday on Load Calculations.
Current Situation:
One 25 KVA transformer is mounted to the utility pole which serves several homes and the machine shop. As noted in the other thread the three phase choices from the power company are 120/240 CT Delta 4 wire or 120/208 Wye 4 wire. The preference that I am leaning toward is the 120/208 Wye since it has the most flexibility and no "wild leg" with the Delta service. My main concern is with the WYE service is whether of not this will affect the single phase service to the homes. Will the power company reconfigure the existing transformer with two more 25 KVA transformers for the WYE service and then the homes will only be able to pull off 120/208 single phase instead of the original 120/240 single phase. This may have adverse effects on water heaters and especially A/C compressors by using 208V instead of 240V? If so, then the better choice for the homes would be for me to go with the Delta to keep the voltage at 240V single phase instead of 208V single phase????
Current Situation:
One 25 KVA transformer is mounted to the utility pole which serves several homes and the machine shop. As noted in the other thread the three phase choices from the power company are 120/240 CT Delta 4 wire or 120/208 Wye 4 wire. The preference that I am leaning toward is the 120/208 Wye since it has the most flexibility and no "wild leg" with the Delta service. My main concern is with the WYE service is whether of not this will affect the single phase service to the homes. Will the power company reconfigure the existing transformer with two more 25 KVA transformers for the WYE service and then the homes will only be able to pull off 120/208 single phase instead of the original 120/240 single phase. This may have adverse effects on water heaters and especially A/C compressors by using 208V instead of 240V? If so, then the better choice for the homes would be for me to go with the Delta to keep the voltage at 240V single phase instead of 208V single phase????