This is my first post her I have tried to search for the topic of this post but have not found a answer to my question so hopefully some you cleaver guys can help me find an answer.
So my problem is as follows:
I doing relay setting in an offshore Windfarm. The Windfarm is operating at 33 kV and the relay I am working with are located on the offshore platform which collects the power generated by the wind turbines.
The relays I working with is the primary protection in the 33 kV array system but is required to provide backup protection on the low voltage side of the 33/0.64 KV turbine transformers.
So to find the correct relay setting I must be able to calculate the 3 phase, 2 phase and single line ground fault currents on LV side of the turbine transformers and refere them to the 33 KV side as that’s the currents my relay will see.
As indicated in the name of this post the 33/0.64 turbine transformer is a three winding transformer which have the following specifications:
HV winding: 33kV 10 MVA
LV1 winding 0.64kV 5 MVA
LV2 winding 0.64kV 5 MVA
The positive sequence short circuit impedance Z% e.g (HV-LV1) is 9.79% and is based on the MVA rating of LV1 winding - 5 MVA so calculating 2 and 3 phase fault currents on the LV side and referring them to the HV side is not a problem!
In the data sheet it is stated that the zero sequence impedance Z0% (HV-LV1 and HV-LV2) is 97.6% each but it is not stated what MVA rating the Z0% is based on.
Do any one have any experience in - or any literature about what the 97.6% relates to?
Is it based on the 10 MVA or 5 MVA rating?
Or is the Zero sequence short circuit impedance Z0= Positive short circuit impedance • 0.976?
Any sparring or assistance is much appreciated
Best regards