Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Three winding transformer parameters

Status
Not open for further replies.

power2023

Electrical
Jan 3, 2023
2
Hi,
I am looking for the typical short circuit impedance and X/R ratio parameters for a three winding transformer for PV connection to grid. The voltage rating for the transformer should be 24.8kV/0.8kV/0.8kV and the power rating is 4MVA/2MVA/2MVA.
Can anyone please help me get an idea of what are the typical ranges.

Thanks!
 
Replies continue below

Recommended for you

X/R ratio for such Solar Transformers is 7-8 (impedance=6.5 %)
 
Oh cool, thanks! Does that mean that Zp-s, Zp-t and Zs-t are all 6.5% roughly?
 
No. Usually, it will be HV-LV1=HV-LV2 = 6.5 % LV1-LV2 = 12 %
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor