I was contracted to design some thrust blocks for a waterworks system. There is an area where they have been requested by the system engineer that seems difficult from a constructability standpoint (the required gravity block where the thrust is upward is much bigger than sketched). Looking at it, I suspect that thrust blocks are not required, but I am not familiar enough with standard practice in this area to be confident. At most, I would be requesting that the client relook a this area, and wouldn't make a judgment on whether they can remove the blocks, given that it's outside my scope of service to evaluate the system as a whole.
This situation is a few close fittings heading into an existing line. It looks to me that the thrust forces should cancel out and you should be able to get away without the thrust blocks or needing to work out effective restraint lengths for the mechanically restrained pipe. The displacement needed to engage the fittings fully and allow the pressure to self cancel should be small. Does this make sense, or are thrust blocks required because the effective restraint length isn't available?
This situation is a few close fittings heading into an existing line. It looks to me that the thrust forces should cancel out and you should be able to get away without the thrust blocks or needing to work out effective restraint lengths for the mechanically restrained pipe. The displacement needed to engage the fittings fully and allow the pressure to self cancel should be small. Does this make sense, or are thrust blocks required because the effective restraint length isn't available?