I am designing a bridge for a private party and the span balance is not good. I have uplift at the abutments. I have not seen a detail for a tie-down before and was wondering if someone could shed some light on this. One abutment has around 15 kips and the other is around 2 kips.
 
Replies continue below

Recommended for you

Design the tie-down as a member subject to tension; add what you believe is an appropriate factor of safety - keep in mind corrosion of the bolts; and check the pullout resistance of the concrete.
 
Skyhook,
It seems the uplift is really small, did you consider adding weight at abutments? If superstructure is integral with abutments? If not, all you need is well-embedded into abutment anchor bolts.
 
AASHTO states the design requirements for hold down devices resisting uplift at substructure units. It is in Chapter 3.17. There is a penalty to be paid when uplift is possible so the approach mentioned by Yakpol would be preferred by many designers.

Dinosaur
 
I'm dealing with the same problem at an expansion bearing. I've decided to carry the force through the end diaphragm with a linkage that allows for the expansion/contraction.
 