I have recently noticed that a lot of structural engineering companies based in Australia give this attached typical details for column ties between floors.
You notice two main thing in that detail:
1) 3 sets of ties at 80 below every slab
2) half the ties spacing at lap length.
I could not find any reference to the above and to be honest it seems arbitrary to me.
my note on tie spacing is the following:
1) For columns with concrete strength equal and under 50 MPa distribute ties equally as per AS3600 c10.7.4
2) design ties to resist shear in columns which most cases would be uniform for lateral loads and thus again tie spacing could be less but still nonetheless uniform throughout the height of the column.
3) Australian concrete detailing handbook recommends adding at least two ties to support bars below ( my take on this, that bars could bend if unsupported during construction)
4) ACI 318-11 7.10.5.2 requires to add bars to resist the horizontal competent force developed in offset bars and place the added ties no more than 6 in from the offset.
Note the detailed of column i attached is for a column not part of a moment resisting frame or high strength concrete column.
This detail is used by too many companies i have seen, and i can't seem to be able to explain their logic!
Thanks for your response in advance and looking forward to hear from you.
You notice two main thing in that detail:
1) 3 sets of ties at 80 below every slab
2) half the ties spacing at lap length.
I could not find any reference to the above and to be honest it seems arbitrary to me.
my note on tie spacing is the following:
1) For columns with concrete strength equal and under 50 MPa distribute ties equally as per AS3600 c10.7.4
2) design ties to resist shear in columns which most cases would be uniform for lateral loads and thus again tie spacing could be less but still nonetheless uniform throughout the height of the column.
3) Australian concrete detailing handbook recommends adding at least two ties to support bars below ( my take on this, that bars could bend if unsupported during construction)
4) ACI 318-11 7.10.5.2 requires to add bars to resist the horizontal competent force developed in offset bars and place the added ties no more than 6 in from the offset.
Note the detailed of column i attached is for a column not part of a moment resisting frame or high strength concrete column.
This detail is used by too many companies i have seen, and i can't seem to be able to explain their logic!
Thanks for your response in advance and looking forward to hear from you.