I work for Tshwane Metropolitan Municipality (Pretoria-SA)and have been asked to investigate the cost effectiveness of the Tiger Extensible Ring Main Units. I don't have enough experience on this but intend to bring up profitable input. The arrangement that we are currently using is the Non-Extensible NX3F 500901. My aim is to compare the possible arrangement which can be very reliable and affordable.
 
Replies continue below

Recommended for you

Hi,Kagiso
Normally we use extensible RMU in two cases :
1. The future network structure is unknown and the client
expects that in will be 1-3 additional feedes in RMU but
the client doesn't know how many.
2. Since each manufacturer of RMU has limited line of non-extensible RMU and the max.number of feeders (functions)in one RMU is usually 4,in case of the client needs for example 6 feeders in one RMU it has two possibility
a) to order two 4-functional RMU and to connect them,loosing
two function in connection or
b) to order one 4-functional RMU + two extentions.
The last option is normally cheaper.
We have the experience with Merlin-Gerin RMU RM6 with SF6
insulation. I havn't enough information about reliability
of extensible since we deliver only few of them whereas
non-extensible - some hundreed.
B.r.
 