Using Expansion Joints in Buildings: Technical Report No. 65 in the southeast USA, do concrete tilt-up buildings with steel joist framing fall under steel buildings?

I tend to think that they do, given that the panels are discrete elements and are not continuous.

Thoughts?
 
Replies continue below

Recommended for you

I'd say they're steel buildings.

Ian Riley, PE, SE
Professional Engineer (ME, NH, VT, CT, MA, FL, CO) Structural Engineer (IL, HI)
 
X3 for steel building. A discrete cross braced wall segment is going to be as stiff as a discrete concrete wall panel. So I think that it comes down to how much expansion and contraction in the deck will occur for the material of construction. And here, the deck is steel.
 
I’m a little confused by the question since I’m not familiar with the technical report you listed.

I am familiar with tilt-up buildings and normally if a tilt-up warehouse is big enough there will be an expansion joint located based off the precast handbook. The joint between panels maybe 2” vs 3/4” at the expansion joint. The roof will need to be configured to allow for the thermal size changes the building will go through.
 