BadgerEngineer
- Sep 16, 2008
- 43
My understanding of how a tilt wall panel should be properly set in the field is the following:
1. The panel is raised and set on shims (on a footing) by a crane.
2. The panel is held until the gap between footing and bottom of panel is grouted & grout is set.
3. The panel is braced and crane removed.
Is this typical practice? A GC is using a different method that inolves setting the panels on shims, bracing, then moving to the next panel before grout is set or before grouting at all. He states it is not economical to wait for the grout to set which I understand.
The prob with this is that the footing no longer acts as a continuous wall footing. It is now point loaded at shim locations (Approximately 4' o.c.) They are seeing cracking in the footing as a result of this.
The GC is stating this is standard practice and tilt wall footings should always be designed for this type of loading. Does anyone have any experience with this? Right now are current solution is to decrease shim spacing to allow the load to be distributed more evenly.
I appreciate all your input.