Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Timber to Timber cantilever connection 3

Status
Not open for further replies.

Aleeeex

Civil/Environmental
Aug 14, 2020
42
Hi,

This is really uncommon to me however I have tried my upmost and was wondering if you would share your thoughts.

I have 2 different sized timber beams cantilevered both which are supported by steel column. The top timber beam overhangs the bottom with a distance of 2.1m from the steel column. I have come up with the following connection. I used 20 M12 and the utilization is 0.89.

I have checked the following

1- bolts capacity perp to the grain
2- timber beams tensile stress along the grain, and shear stresses.

image_rvvqlu.png


Bending Moment

image_zc5sxa.png


Shear

image_t91c9x.png


Thank you for your input.
 
Replies continue below

Recommended for you

If the lower beam is supported by another cantilevered beam at its end then your model and deflection are not correct. You probably need to model this in 3D to begin to get accurate results.

My Personal Open Source Structural Applications:

Open Source Structural GitHub Group:
 
Celt83 said:
If the lower beam is supported by another cantilevered beam at its end then your model and deflection are not correct. You probably need to model this in 3D to begin to get accurate results.

The lower beam is supported by a pair of columns unless the structure has changed. No need for a 3D model.

BA
 
Status