I realise this might not be the correct location to ask this question, but maybe other engineers have run into a similar problem.
We are currently preparing to carry out structural steel repairs to the base of a furnace in a petrochemical facility. To complete the repairs we need to remove the fireproofing. Is there any guidance on how long the fireproofing can be removed for, 2weeks, 2 months, 2 years? Maintaining fireproofing throughout seems unrealistic. I know for temporary conditions, say a temporary foundation to dress a tall vessel before you crane it into position, can be designed for reduced wind and seismic loads. These reductions are based on duration and must take into consideration some level of risk. I am hoping there is something similar for fire rating.
The ideal repair process is as follows:
1. Remove a small portion of fireproofing
2. Test material thickness
3. Provided engineered detail and reinforce, if necessary.
4. repeat steps 1-3 possibly 5-10 times (this may take some time)
5. Removing all fireproofing at once is not possible as the steel is heavily corroded and we are concerned the concrete fireproofing may be providing some form of lateral restraint to the steel. Therefore we open a small section then repair and keep moving along.
6. All steel will need to be cleaned and painted at the end once strength requirements are satisfied.
7. Repair Fireproofing.
I realise this might not be the correct location to ask this question, but maybe other engineers have run into a similar problem.
We are currently preparing to carry out structural steel repairs to the base of a furnace in a petrochemical facility. To complete the repairs we need to remove the fireproofing. Is there any guidance on how long the fireproofing can be removed for, 2weeks, 2 months, 2 years? Maintaining fireproofing throughout seems unrealistic. I know for temporary conditions, say a temporary foundation to dress a tall vessel before you crane it into position, can be designed for reduced wind and seismic loads. These reductions are based on duration and must take into consideration some level of risk. I am hoping there is something similar for fire rating.
The ideal repair process is as follows:
1. Remove a small portion of fireproofing
2. Test material thickness
3. Provided engineered detail and reinforce, if necessary.
4. repeat steps 1-3 possibly 5-10 times (this may take some time)
5. Removing all fireproofing at once is not possible as the steel is heavily corroded and we are concerned the concrete fireproofing may be providing some form of lateral restraint to the steel. Therefore we open a small section then repair and keep moving along.
6. All steel will need to be cleaned and painted at the end once strength requirements are satisfied.
7. Repair Fireproofing.