2easyg
Marine/Ocean
- Dec 22, 2016
- 2
Hello All
I have been challenged on my knowledge of compressed air systems which has caused me to pause and consider that I might be blindly following consensus without adequate understanding.
The question is relatively simple, calculate the time to fill the following receivers:
I have 2, 400 gallon receivers that I need to fill to 175 PSIG from empty (0 PSIG) with a reciprocating air compressor rated at 26 ACFM at 175 PSI, with a sub note indicating the ACFM is FAD tested in accordance with ISO 1217.
In the past, I have assumed that the 26 ACFM is the amount of free air entering the compressor to deliver 175 PSI. I would convert the ACFM to SCFM from the estimated location the compressor was tested and then SCFM to ACFM to where the compressor will be operating.
I would then apply the formula:
t = (V(total receiver) * (Psig(final) + Psi(atm))) / (Psi(atm) * ACFM)
t = ((107 Cu Ft) * (175 + 14.7 - 14.7)) / (14.7 * 26) = ~ 50 mins.
However, I have recently been asked why include the pressure ratio when the definition of ACFM is the CFM at the tested environmental conditions at the outlet of the compressor, as defined on engineeringtoolbox.com. If the compressor rating is indeed pushing 26 CFM at 175 PSI, then indeed there is no reason to include the pressure ratio and since the pressure of the tanks are the same as the pressure rating of the compressor. The time to fill would neglect the pressure and just be Receiver Volume / Volumetric flow. Essentially, filling up a bucket.
Additionally, I have been told that to use the above formula, I would have to convert the ACFM to "free air" conditions, i.e.:
Free Air Flow = 26 CFM * (175 + 14.7) / 14.7 = 335.52 CFM
then
t = ((107 Cu Ft) * (175 + 14.7 - 14.7)) / (14.7 * 336) = ~ 3.8 mins.
I guess that I haven't previously questioned the idea that all compressors are rated from a standard ambient condition. Are different types of compressors rated differently? Could the same type of compressor be rated different ways for different applications?
So if someone with air compressor expertise could give me a hand with clearing out the confusion, it would be most appreciated. Perhaps suggesting a good text on the subject?
Cheers,
I have been challenged on my knowledge of compressed air systems which has caused me to pause and consider that I might be blindly following consensus without adequate understanding.
The question is relatively simple, calculate the time to fill the following receivers:
I have 2, 400 gallon receivers that I need to fill to 175 PSIG from empty (0 PSIG) with a reciprocating air compressor rated at 26 ACFM at 175 PSI, with a sub note indicating the ACFM is FAD tested in accordance with ISO 1217.
In the past, I have assumed that the 26 ACFM is the amount of free air entering the compressor to deliver 175 PSI. I would convert the ACFM to SCFM from the estimated location the compressor was tested and then SCFM to ACFM to where the compressor will be operating.
I would then apply the formula:
t = (V(total receiver) * (Psig(final) + Psi(atm))) / (Psi(atm) * ACFM)
t = ((107 Cu Ft) * (175 + 14.7 - 14.7)) / (14.7 * 26) = ~ 50 mins.
However, I have recently been asked why include the pressure ratio when the definition of ACFM is the CFM at the tested environmental conditions at the outlet of the compressor, as defined on engineeringtoolbox.com. If the compressor rating is indeed pushing 26 CFM at 175 PSI, then indeed there is no reason to include the pressure ratio and since the pressure of the tanks are the same as the pressure rating of the compressor. The time to fill would neglect the pressure and just be Receiver Volume / Volumetric flow. Essentially, filling up a bucket.
Additionally, I have been told that to use the above formula, I would have to convert the ACFM to "free air" conditions, i.e.:
Free Air Flow = 26 CFM * (175 + 14.7) / 14.7 = 335.52 CFM
then
t = ((107 Cu Ft) * (175 + 14.7 - 14.7)) / (14.7 * 336) = ~ 3.8 mins.
I guess that I haven't previously questioned the idea that all compressors are rated from a standard ambient condition. Are different types of compressors rated differently? Could the same type of compressor be rated different ways for different applications?
So if someone with air compressor expertise could give me a hand with clearing out the confusion, it would be most appreciated. Perhaps suggesting a good text on the subject?