I've been watching this post for a number of days. My previous post, while considered by some to be rude or curt, was accurate. The original posting never told me the sprinkler K factor, the arrangement of the tires, and the clearance between the tires and the sprinkler.
This again is another scenario where ESFR sprinklers are believed to be the panacea of all fire protection designs. Why? Look at Table 12.4.2 (d) of NFPA 13. When a Table contains a footnote for one design that states Where used in this application, ESFR protection is expected to control rather than suppress the fire. What the heck? That does not sound like the definition of fire suppression in Section 3.3.10. Footnotes like this don't inspire confidence in my mind.
Frankly, I believe this another instance where the NFPA 13 committee read one fire test report, said it worked, and plugged it into the code. I reviewed FM Data Sheet 8-3 and the options are far more limited. This, in my old school, fuddy duddy, old fart mind needs in-rack sprinklers to provide for a reliable, safe design. Yup, it sucks to specify in-rack sprinklers. But this is one of a few commodities I feel that we should be very conservative in our designs.
When FM states they have little experience I tend to tighten up the design, and they clearly state this in Data Sheet 8-3.
In the late 1980s-early 1990s the tire industry did research on waste tires because of the rash of tire fires before recycling regulations were enacted. One of the more interesting facts of that research was that a single tire released close to 2 pounds of heavy (i.e., large molecules of hydrocarbons) oil when consumed in a fire. Introducing a combustible liquid in a fire is very challenging - combine it with ESFR tells me that we have a real potential for losing the building if ESFR is used because the oil can be carried by the sprinkler water and cause a large number of sprinklers to operate. This research, at least in my mind, drives my decision as to the importance of in-rack sprinklers.
I hope my comments are not perceived as a rant and I apologize if anyone feels hurt by my comments. But as someone who started his career on the front end of 1 1/2 inch hose line fighting fires and responded to two incidents where firefighters died, I tend to take sprinkler design very, very seriously.