TJI w/ web stiffeners flexural strength 1

Status
Not open for further replies.

cbinder

Structural
Nov 14, 2018
10
A contractor approached me about a fix for a house I designed. Specifically, the stairs don't meet minimum head heights. What he wants to do is stiffen the web on both sides with 1" plywood, provide a small stud pack on either end of the span and then cut out 5 inches of the joists depth. Obviously, this would:
1) remove the bottom tension chord from the TJI and a few inches of the web.
2) turn that 4' span into a composite beam

The load pathing of the proposed fix all makes sense and will work, my only question is how would I go about determining the allowable bending stress of that composite. Total thickness and depth of the remaining wood would be 2 3/8"x6". Our wood species of choice is Douglas Fir Larch.

Thank you in advance for any advice
 
Replies continue below

Recommended for you

I'd be inclined to discount the TJI remant entirely and evaluate the member assuming that the two 1" pieces of plywood are all that there was s to it. You know, if that works.
 
That was one option I was thinking, but I don't know where I can find the allowable bending stress of plywood.
 
As one who recently went down the rabbit hole of TJI reinforcing, DON'T DO IT. When you start messing with these things they don't come back very easily. I didn't look into flange damage all that closely (I was concerned with a damaged web), but from the little I did look at that it was typically worse than web damage.

Here's a link to the thread I had on the topic. Near the end I post a link to a PhD dissertation that looks at both web and flange cuts.

I would strongly suggest adding the studs, cutting the TJI back to bearing on each side (along with necessary bearing details, etc.) and add a new member that is the correct depth - be it dimension lumber, LSL, LVL, etc.
 