Good Morning fellow engineers,

I am working on a toe guard of guard rail the code requirements says

The toe guard shall be securely fastened and have a height not less than 100mm (4") above the working surface.

My question is if I run a Unistrut 1 5/8" as a toe guard and leave 2 3/8" between surface and bottom of Unistrut. I am satisfying the 4" above working surface criteria. Is it code compliant?
IS there any document clearly saying that it should be a flat plate and must touch the working surface?


 
Replies continue below

Recommended for you

the intent of a toe guard is to prevent objects from falling on workers below, leaving a large gap between the surface and rail you are proposing doesn't seem like it would fulfill it's purpose.

My Personal Open Source Structural Applications:

Open Source Structural GitHub Group:
 
I agree with Celt - I usually specify a 4" angle or flat bar (depending on support conditions and spacing) as a toe guard/toe kick. I'll specify enough of a gap so the walkway won't hold water, but that's about it.
 
I see.

Thank you very much guys
 
[URL unfurl="true" said:
https://www.osha.gov/laws-regs/regulations/standardnumber/1917/1917.112[/URL]]1917.112(d)
Toeboards. Toeboards shall be provided when employees below could be exposed to falling objects such as tools. Toeboards shall be at least 3½ inches (8.9 cm) in height from top edge to floor level, and be capable of withstanding a force of 50 pounds (222 N) applied in any direction. Drainage clearance under toeboards is permitted.

[URL unfurl="true" said:
https://www.dir.ca.gov/title8/1621.html[/URL]](b) A standard toeboard shall be 4 inches (nominal) minimum in vertical height from its top edge to the level of the floor, platform, runway, or ramp. It shall be securely fastened in place and have not more than 1/4-inch clearance above floor level. It may be made of any substantial material, either solid, or with openings not over one inch in greatest dimension. Toeboards shall be provided on all open sides and ends of railed scaffolds at locations where persons are required to work or pass under the scaffold and at all interior floor, roof, and shaft openings.

The intent that there shall be minimal gap between the bottom edge of the toeboard and the flooring is pretty clear