I operate a fleet of boats with halogen flood lights on them and have been experiencing a lot of failures of the toggle switches. Each wlswitch operates two 500w halogen bulbs at 120v. Well I found out that light bulbs have a tremendous inrush current so even though the switch exceeds the resistive rating they also have a much lower "lamp" rating that is seldom spoken of.
All of that said I will be installing switches with silver/cadmium contacts but they still don't have sufficient ratings. Would it be reasonable to buy two pole switches and run the load in parallel through the switch to increase the rating? I'm trying to avoid any rewiring or relay installation.
All of that said I will be installing switches with silver/cadmium contacts but they still don't have sufficient ratings. Would it be reasonable to buy two pole switches and run the load in parallel through the switch to increase the rating? I'm trying to avoid any rewiring or relay installation.